Logo VM parameter mapping
#2
I have figured this out.

There seems to be a "bug" in the Siemens Logo8.3.

When a parameter has the address Word :0 the modbus address is 0
When a parameter has the address Word :2 the modbus address is 1
When a parameter has the address Word :4 the modbus address is 2

So you always have to divide the address by 2.

The same happens with a Dword.

I figured this out by checking the values with qModMaster
Reply